I am doing some work at my house and I am honestly getting fed up with conflicting shit I get from friends/family/guy at rona, etc.
I know the right answer is somewhere in the middle, but here goes.
My house currently has an 125amp panel (main) from the street with a few more breaker openings.
My objective is to run another stove in my basement, a fridge, and a few more outlets for microwave/toaster/etc. as I am putting a small kitchen downstairs.
To buy breakers for my existing panel is expensive, I don’t have exact prices since I don’t have internet and haven’t checked. I will check tonight to find out the exact cost of breakers for my original panel.
In the meantime a friend gave me a 100 amp panel with breakers for free, the idea is to use this as a sub panel to power my little kitchen stove/outlets. Generally you’d use 60amp, but since this one is free I figured 100 amp will suffice.
The issue: is it to code? Well here is the cluster fuck I am getting into. I am told that if I run a 100amp sub panel even though it will only have a stove and a few outlets I’d have to run a really thick wire (3 guage as per Rona guy – who refused to sell it to me WTF????) as if I was servicing a fully loaded 100 amp wire. The reason is that if I sell the house and people see the open breaker spots they will use them.
I told him that I can blank them off, whatever I will only use it for stove/etc. It become a d!ck measurement contest, he may be right, I don’t know so I left.
What I need to know is can I pass inspection (electrical for my insurance company) by running a 100 amp pony panel if I am only utilizing very few breakers? If so, what guage wire do I need to run to it from the main panel?
Other options:
Get 200 amp panel from other friend for free, get city to change my service to 200amp. Conduit size is already made for that as homes here can be fairly sized. This is the most expensive options, but not a bad one and probably “cleanest”
Run a real 60 amp panel, but I’d be paying upwards of $300+ for the panel and breakers to do the exact same thing that my 100 amp donated one will do, which includes breakers and it’s free.
What the FAWK am I supposed to do? Sorry for the long rant, just getting fed up with this bullshit.
|
Top
|
|
|
|
#5810565 - 09/19/11 01:35 PM
Re: Eletrical/DIY gurus.
[Re: Risk E. Business, esq.]
|
CivicGSR50
Poster
Registered: 01/14/10
Posts: 243
|
Vasoline, Don't worry about the butt-hurt you're experiencing right now. I've got the same thing at my place, 100 amp main, and a separate pony panel, yes with a 3 gauge wire. Mine was up to code, and got it inspected, the only difference is that once I upgraded from Knob and Tube, I installed ground fault breakers, that was upto and beyond code for bedroom wiring. Theres two electrical supply companies on Denison near Vic Park, they'll sell you everything/anything. Oh yeah, they're former electricians on staff as well.
PM me your bbm, i'll take a pic of my setup tonight, visual is everything. Buy new panel, add pony panel, do it all one time right. No No, we do not MAKE IT RIGHT..
|
Top
|
|
|
|
#5810606 - 09/19/11 02:01 PM
Re: Eletrical/DIY gurus.
[Re: loudsubz]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
I want to do this clean and proper without spending a fortune. By the way thanks for the advice you gave me before!!!
Where did you recommend I get a breaker for my main panel since i need one feed to go into the sub?
What wire guage should I use from my main to the pony panel?
|
Top
|
|
|
|
#5810615 - 09/19/11 02:06 PM
Re: Eletrical/DIY gurus.
[Re: Risk E. Business, esq.]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
Another thing to note is that I will be doing a natural gas stove on my main floor in a few years time. Eventually the basement stove will also be natural gas so I do plan on reducing the electrical load on the panel.
|
Top
|
|
|
|
#5810630 - 09/19/11 02:12 PM
Re: Eletrical/DIY gurus.
[Re: loudsubz]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
Matt, for my pony panel should i treat it as a 60amp or a 40 amp, i will have to change the main breaker on it right or no? For stove and misc outlets what should I change it to if i have to change it?
|
Top
|
|
|
|
#5810643 - 09/19/11 02:17 PM
Re: Eletrical/DIY gurus.
[Re: Risk E. Business, esq.]
|
Senor Eduardo_82
miataist
Post Master Supreme
Registered: 01/09/03
Posts: 38067
Loc: Ca�ada
|
Monster Cables
|
Top
|
|
|
|
#5810693 - 09/19/11 02:45 PM
Re: Eletrical/DIY gurus.
[Re: Euphoricuck]
|
Screamin' Type-R
The R stands for exactly what you think it does.
Post Master Supreme
Registered: 02/20/01
Posts: 48088
Loc: T.O. - Canaduh
|
coat hanger. better electron flow
*dead*
_________________________
 "Ban low performance drivers, not high performance cars"
|
Top
|
|
|
|
#5810912 - 09/19/11 04:11 PM
Re: Eletrical/DIY gurus.
[Re: robbbby]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
Thanks for clarifying that!!!
Man I know it’s simple, but it still specialized enough where you really need to be in the trades with experience to know all this little stuff.
So I have to price out a 60amp breaker for my main and then I will just run the 6/3 into the pony panel which has a 100 amp breaker on it.
This is where the Rona guy confused me, fawking moron. He told me I’d overload the wire and set the house on fire.
I will take pics tonight, hopefully I get my internet up and working.
|
Top
|
|
|
|
#5810917 - 09/19/11 04:13 PM
Re: Eletrical/DIY gurus.
[Re: Risk E. Business, esq.]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
robbby does it matter how long the run of 6/3 is to the pony panel to be up to code? What's NMD90 mean? My pony panel is about 10 ft away from the main.
|
Top
|
|
|
|
#5810924 - 09/19/11 04:16 PM
Re: Eletrical/DIY gurus.
[Re: Risk E. Business, esq.]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
Also, is 60amp breaker ok to run on my 125amp service?
Should I go down to 40amps so it's a 40amp pony panel? Is a 40amp enough for a stove and misc plugs?
|
Top
|
|
|
|
#5810960 - 09/19/11 04:37 PM
Re: Eletrical/DIY gurus.
[Re: robbbby]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
Main panel is siemens. i will post pics later tonight.
|
Top
|
|
|
|
#5811751 - 09/19/11 10:32 PM
Re: Eletrical/DIY gurus.
[Re: Simon_the_Pieman]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
loudsubz is right, it's not siemens it's sylvania. I was thinking siemens because everything HD and Rona is.
My bad
Here are pics of my situation. I got the 6/3 wire, i think i fucked up and got it too short, FUCK!!! 60 dollars down the drain.
Anyway, on to the pics:
main panel

Main panel with cover

main panel label

Room and wire run to sub panel from main

wire run into sub panel

sub panel

looking from kitchen into living room toward sub panel and main panel

Picture of space, sub panel on left wall

Moved sub panel 16" over to see if 6/3 wire is long enough 

pic of main panel and 6/3 wire, probably not long enough, FUCK FUCK FUCK FUCK
|
Top
|
|
|
|
#5811764 - 09/19/11 10:37 PM
Re: Eletrical/DIY gurus.
[Re: Risk E. Business, esq.]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
Moral of the story....don't buy an old house 
p.s. i wouldn't have it any other way!
|
Top
|
|
|
|
#5812164 - 09/20/11 08:38 AM
Re: Eletrical/DIY gurus.
[Re: Euphoricuck]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
I am going to try and return the cable i bought from HD and replace it with a longer one, I want to be as clean and up to code as possible.
Here are additional pictures:
main breaker on sub panel




Main panel close up

|
Top
|
|
|
|
#5812706 - 09/20/11 01:19 PM
Re: Eletrical/DIY gurus.
[Re: Risk E. Business, esq.]
|
c2k
Post Master Supreme
Registered: 05/21/00
Posts: 19349
Loc: Wiesloch-Walldorf, Germany
|
Moral of the story....don't buy an old house  p.s. i wouldn't have it any other way!
hell no. buying an old house means fixing it up the way you want it rather than builders cookie cutter style with same shit on the street.
all i can say is, welcome to the homeowner life, it will get better! take a shitload of pics of before and after and after you're done you'll go DANG.. I did all that?
_________________________
Who cares
|
Top
|
|
|
|
#5812909 - 09/20/11 02:34 PM
Re: Eletrical/DIY gurus.
[Re: Screamin' Type-R]
|
f22b-dohc
Post Master Supreme
Registered: 09/09/05
Posts: 11227
Loc: canadia
|
coat hanger @ 45 degree angle. better electron flow *dead*

bah, i went to a gf's friend who bought an old house by the beaches...it was a demolition day thing.
BFH, and smash all the walls - take your agression out day.
we got to the ceilings on the first floor....--took it off to find another above it.. LOL.
who ever reno'ed just built another ceiling over the old...
_________________________
JB weld is your friend Chewbacca makes me yawn *Yawn* "rolling -----on my 2.0, with the rag top down so my hair can blow..."
|
Top
|
|
|
|
#5813197 - 09/20/11 04:44 PM
Re: Eletrical/DIY gurus.
[Re: loudsubz]
|
robbbby
master electrician
Post Master Supreme
Registered: 01/23/02
Posts: 15430
Loc: Canada
|
butt splice, heat shrink, 1ft of wire and you're there! For this he would need an accessible junction box and proper marettes etc.
technically with #6 you aren't allowed to use marettes, needs to be a compression fitting like a split bolt.
|
Top
|
|
|
|
#5814355 - 09/21/11 10:02 AM
Re: Eletrical/DIY gurus.
[Re: robbbby]
|
Risk E. Business, esq.
Provides a Great Work Environment.
Post Master Supreme
Registered: 05/17/10
Posts: 46502
|
Thanks, I bought a longer 6/3 and it's all fixed. No pix yet, had to pour concrete last night to fix my drains and moved patio stones until 1 am.
|